Shutdown mode #229
Replies: 2 comments
-
Hi, The shutdown logic can be found here: ROSCO/ROSCO/src/ControllerBlocks.f90 Line 383 in 41f2c00 The collective pitch angle triggers a shutdown. Once it's shut down, it stays shut down. If you have suggestions for logic updates, please share them or contribute them to the code. A soft cut-out could be implemented with code from #170, but it's not fully supported yet. Best, Dan |
Beta Was this translation helpful? Give feedback.
-
I've been reviewing some of the discussions posted, and I noticed that another was turned into an Issue given the development efforts to support all DLCs (discussion #317 ). I would suggest that having the proper wind speed shut down/restart behavior is a critical component for system loads and that the 61400-1/-3 standard highlights many DLCs where simulating at V_out is required for that very reason. Unfortunately, I have nothing to offer here other than highlighting the need for such controller logic. |
Beta Was this translation helpful? Give feedback.
-
I'd like to model the dynamics around cutout, ie when the turbine is moving in and out of its shutdown position, but I can't find any documentation about how the ROSCO shutdown mode works. Does it just feather off the blades once the filtered blade pitch signal reaches SD_MaxPit? If the blades are individually controlled, will it react to any blade? I saw a comment that the turbine can't restart after a shutdown -- is that true? It seems... unrealistic.
If this information is published somewhere I'd be very glad to be pointed in that direction. Thanks for your help.
Beta Was this translation helpful? Give feedback.