Hi, I realized, that on Defrost I have Pressure surges in the pipe for Floor heating, I think because the HP raises the flowrate which I don't have any possibility to reduce as it seems. regards ede |
Beta Was this translation helpful? Give feedback.
Replies: 3 comments 6 replies
-
Hi |
Beta Was this translation helpful? Give feedback.
-
Second question, have you tried it out already during a defrost cycle to change the operating mode in the controller? Does it work? |
Beta Was this translation helpful? Give feedback.
-
I think it would be best to predict defrost, and before defrost switch heating.. |
Beta Was this translation helpful? Give feedback.
Hi Ed,
I'm not sure why, but after 2 days now my script finnally started to work as expected, as soon aos DEFROST is triggert, OP-Mode switches to DHW and on DEFROST Finish, OP-Mode switches back to HEAT. I don't see why it did not work directly as I didn't change it the last days. But I see the root cause is my old existing pump in the Heating system, it does not hande the high volume of the HP-internal Pump when DEFROSTING. So I will try to find a replacement pipe for that pump and see, if the internal HP pump is strong enough.
Thanks.
regards
ede