Maximum force charge kw amount limited to 6kw #537
-
Not sure if I am doing something wrong, but the max force charge amount seems to be limited to 6kw. Is there a reason for this? Can it be set to more? With a 20.8kw battery system being depleted to 20%, the 6kw of force charge amount is too low. Thank you! system |
Beta Was this translation helpful? Give feedback.
Answered by
canton7
Feb 7, 2024
Replies: 1 comment 11 replies
-
Unless I'm vastly misunderstanding something, you've got a H1-5.0, which can output 5kW? |
Beta Was this translation helpful? Give feedback.
11 replies
Sign up for free
to join this conversation on GitHub.
Already have an account?
Sign in to comment
The power of your inverter is how quickly it can turn AC current into DC current, and vice versa (simply put).
The battery is DC. Mains, and the grid, is AC. Therefore to charge the battery from the grid you need to turn AC into DC, and to discharge the battery to the grid you need to turn DC to AC. Both of these operations are therefore limited by the power of your inverter.
Force discharge discharges the battery to the grid. The speed at which you can do this is limited by your inverter size.