This can be done. First make sure you have setup the humidity sensor with the correct alarm and limit values. I would start with limit values of 0 and 100. Than set the alarm values to the values you want to have in your house. The max alarm value will be used to trigger the relay. So lets say you want no more than 60% humidity, set the alarm max value to 60. You should create an enclosure. Called it 'home' as it is your home you want to control Then select the Save the form. This should do it. The outlet goes on when the high alarm is reached, and shutdown when the low alarm value is reached. |
Beta Was this translation helpful? Give feedback.
This can be done.
First make sure you have setup the humidity sensor with the correct alarm and limit values. I would start with limit values of 0 and 100. Than set the alarm values to the values you want to have in your house. The max alarm value will be used to trigger the relay. So lets say you want no more than 60% humidity, set the alarm max value to 60.
You should create an enclosure. Called it 'home' as it is your home you want to control
Then create an area with
humidity
typeSelect
sensor
modeSelect the sensor(s) you want to use
Then select the
high alarm
tab and select the relay for your dehumidifier.Save the form.
This should do it. The outlet goes on when the high alarm is r…